| Parameter | Value | Remarks |
| PD013 | 08 | Reset parameters to factory defaults. Do this first. |
| PD001 | 1 | Uses external terminal |
| PD002 | 1 | Uses analog voltage for speed control |
| PD003 | 50.00 | Main frequency. |
| PD004 | 50.00 | Base frequency. |
| PD005 | 100.00 | Maximum operating frequency. |
| PD006 | 2.50 | Intermediate frequency. Used for torque compensation. |
| PD007 | 0.50 | Minimum frequency. Used for torque compensation. |
| PD008 | 220 | Maximum voltage. This is suitable for delta connected motor. |
| PD009 | 24.00 | Intermediate voltage. Maximum torque boost at low RPM. |
| PD010 | 8.00 | Minimum voltage. Maximum torque boost at low RPM. |
| PD011 | 10.00 | Minimum operating frequency. |
| PD014 | 2.50 | Acceleration time. |
| PD015 | 2.50 | Deceleration time. |
| PD072 | 100.00 | Maximum frequency the potentiometer can set. |
| PD073 | 10.00 | Minimum frequency the potentiometer can set. |
| PD044 | 02 | (FOR) terminal is forward. Exchange values with PD045 if motor runs the wrong way. |
| PD0045 | 03 | (REV) terminal is reverse. Exchange values with PD044 if motor runs the wrong way. |
| PD046 | 04 | (RST) terminal is stop. Note that this terminal works the other way around. Contact is opened to stop. |
| PD047 | 14 | (SPH) terminal is reset. Used to recover a tripped VFD. |
| PD049 | 13 | (SPL) terminal is emergency stop. Used to keep the motor from starting if spindle cover is open. |