Jonny,
I'm way up in West Yorkshire. But thanks for the offer.
Also I wondered if your converter may be a bit over kill.
The plate on the motor says 1.5 Amp FLC . I assume that means Full Load Current.
Looking at the calculations for three phase motor power power consumption I get, using an average Voltage of 415 and an assumed power factor of 0.8, a power draw of only 0.863 Kw.
So a little 2.5 Kw unit would do fine.
I'd be happy for anyone to confirm these figures.
Dave.