Lathe Jaguar VXS inverter - remote pendant

<< < (6/7) > >>

John Rudd:
My thoughts on nvr....
A true no volt release switch assembly should be wired in the primary side .....As it says, if power is lost, it releases....no auto restarts, no surprises...

My experience with inverters/vfd's.....most I've come across, Imo, Teco,(jaguar is just a model...) Invertek etc....all require a maintained input not fleeting for external switching.....stop/start and fwd/rev switches should be mutually exclusive....that is one state or the other.....

appletree:

--- Quote from: John Rudd on October 30, 2015, 04:38:49 PM ---My thoughts on nvr....
A true no volt release switch assembly should be wired in the primary side .....As it says, if power is lost, it releases....no auto restarts, no surprises...

My experience with inverters/vfd's.....most I've come across, Imo, Teco,(jaguar is just a model...) Invertek etc....all require a maintained input not fleeting for external switching.....stop/start and fwd/rev switches should be mutually exclusive....that is one state or the other.....

--- End quote ---
I have a soft spot for Mitsubishi freqrol inverters (I bought my first for £2) I am quite adept at programming these and they can be programmed for fleeting input signals thus effectively providing no volt release on supply failure. Crazy I know but i have 9 inverters from various manufacturers though some are only 200w. I have 2 off Jaguar VXS inverters which I want to fit to my wood turning lathes Maintained switching is not an issue but I like to do things “properly” if feasible. Regards

Thanks for your input Hopefuldave. Collectively I can see the way forward, The future is Mitsubishi appletree

raynerd:
 :doh:

Gutted, awful feeling of two wasted hours before bed - my first efforts produce an OH2 external trip alarm input!!

I've attached the circuit I am using, only mine is 24v internal and therefore a 24v relay. I've also attached the error flow diagram. I'm not clear about the THR issue... There Is a wire collecting THR to 24v. When it was manual it was hard wired 24v to THR to FWD - is that right, it suggestions so in the flow diagram.

The inverter boots up ok, as soon as I hit RUN on the new controller I hear the relay switch but then the inverter immediately errors with the trip OH2.


raynerd:
Nooooooo.... Found another jaguar specific circuit online and spent an hour making it... Same OH2 error!! Time to go and sulk for the afternoon. Anyone any suggestions at all before I try again this afternoon?

David Jupp:
OH2 error indicates open circuit between P24 and THR - see control circuit section of the manual that I previously linked to.